Still confused regarding frame grounding for AC and DC.

Anything electric, AC or DC

Postby IraRat » Tue Sep 20, 2005 1:52 pm

Okay, Steve. Your answer wasn't simple enough for this moron here. I thank you, but could you please try again and consider the following:

1) Look at that link again, for "our" panel, because I don't understand the descriptive.

http://www.boatersworld.com/webapp/wcs/ ... escription

It's listing more circuits than I see on the box. I only see a main breaker, and 3 other lines This is all I NEED for the 3 lines I plan to run.

So I just don't get it. I think BoatersWorld site may be incorrect. Does yours look exactly like this one, and does it match the specs as they state them?

2) Frame Grounding:

Let's say that this weekend, I want to attach and test all of my cabin lights, porch lights, receptacles, etc. WITHOUT having this panel yet.

I actually started this this PAST weekend, just connecting the right cabin light, but all I did was take my main "right daisy chain" feeder lines, temporarily connected them to a plug, and stuck it into an extension chord running to the house.

Remember--no panel yet. But lo and behold, I had light. I attached positive, negative, and ground. So now I have to daisychain the rest of my devices, all with separate grounds.

If I decided to ground to the frame, do I just ground it from the PANEL, or are you saying I should be doing something regarding connecting the individual devices/outlets? I hope this AIN'T the case, because the way wires are just sticking out of the wall now, I don't see any way to attach anything directly to the frame from there.

Ooops. See, I TOLD you: My head just exploded.

And Dale, if you ever feel bad about your electrical knowledge, just think of me.
--Ira

"My HD and Wal-Mart have been out of Titebond for weeks, and I think it's a communist conspiracy."
User avatar
IraRat
Forum Storyteller
 
Posts: 1573
Joined: Wed Apr 06, 2005 8:43 am
Location: South Florida

Postby Steve_Cox » Tue Sep 20, 2005 2:26 pm

Ira, "our panel" in the picture has 4 breakers and 3 plugged holes for future breakers... top one is the main breaker the ones under that are the branch circuits. My panel dosen't look exactly like it the faceplate is black. The panel will have a terminal on each branch circuit for the hot wire for each device. It will also have a neutral bus and a grounding bus. That means just a metal bar with screws in it to bolt the wires for neutral and ground. It will also come with a wiring diagram which you will be able to figure out. You arn't going to like the fact that you should have 3 wires running to each outlet or device. Key word is should, will it kill you if you don't? probably not. THe panel will work just like the way you tested your lights with two wires, should you do it that way? No. It will work? Yes. Do I care if there is no ground wire? Not really. But, if you have a bare wire in any of your lights and it has a metal frame and one of your kids touches it, it will probably be the last time they or your wife will ever be in the teardrop. She will se to that. I don't know if I answered your questions. My head is starting to hurt...

Steve :?
Steve
User avatar
Steve_Cox
4000 Club
4000 Club
 
Posts: 4903
Images: 196
Joined: Sun Apr 03, 2005 8:46 am
Location: Albuquerque New Mexico

Postby IraRat » Tue Sep 20, 2005 2:50 pm

I have three wires for each line, so I can daisy the ground just like I'm daisying the positive and negatives?

I also promise to let this avatar only live for a day or so, because it will SURELY give you a headache.
--Ira

"My HD and Wal-Mart have been out of Titebond for weeks, and I think it's a communist conspiracy."
User avatar
IraRat
Forum Storyteller
 
Posts: 1573
Joined: Wed Apr 06, 2005 8:43 am
Location: South Florida
Top

Postby Ken A Hood » Tue Sep 20, 2005 2:59 pm

I would hope that is ANYONE has any doubts about doing their own wiring; or are uncomfortable about trying to wire it will take it( and the accessories/panel etc...) to a qualified service center.

You could always do alot of the setup yourself; running wire to your accessories( fans/lights...etc) locating the panel/battery; roughing in lights/switches, but let the pro's do the actual wiring up to finish the installation...
Disclaimer: I in no way resemble the avatar shown. Furthermore, I in no way have any affiliation to the Trailer Park Boys and more specifically Bubbles!
User avatar
Ken A Hood
500 Club
 
Posts: 841
Images: 42
Joined: Sun Apr 18, 2004 8:15 pm
Location: ON CANADA
Top

Postby Steve_Cox » Tue Sep 20, 2005 4:05 pm

Ken A Hood wrote:I would hope that is ANYONE has any doubts about doing their own wiring; or are uncomfortable about trying to wire it will take it( and the accessories/panel etc...) to a qualified service center.

You could always do alot of the setup yourself; running wire to your accessories( fans/lights...etc) locating the panel/battery; roughing in lights/switches, but let the pro's do the actual wiring up to finish the installation...


Good advise Ken, would you consider a knowledgable and experienced friend almost as good as a qualified service center/Pro? I think Ira could probably find some good help in South Florida, lots of qualified Boat and RV electrical types there that just love cold Bud..

Steve
Steve
User avatar
Steve_Cox
4000 Club
4000 Club
 
Posts: 4903
Images: 196
Joined: Sun Apr 03, 2005 8:46 am
Location: Albuquerque New Mexico
Top

Re: On AC frame grounding

Postby bdosborn » Tue Sep 20, 2005 6:24 pm

Steve_Cox wrote:Hypothetically writing. On your AC power the neutral and the ground are bonded together and the ground is bolted to the frame. You go to "Poppy's by the Tree" campground and it turns out Poppy is an amateur electrician. You get the campsite with reverse polarity (all Poppy's campsites have reverse polarity). You set up and plug in your power cord. You go to take your bicycle off the tongue mounted bike rack and suddenly you find that you can't let go of the handlebars because you're getting about 112 of the 117 volts available right into your continuously constricting muscles in your hands. Don't you wish for a split second you hadn't tied the ground to the frame as you feebly jump into the air to get your wet bare feet off the damp ground and break the circuit?

Steve in St Augustine 8)

PS - I'm building a woody teardrop and have a ground wire to my frame. I also have a "reverse polarity " warning light on my AC electrical panel. There are lots of Poppys out there in the world.


First off, you never, ever bond the neutral to the ground wire in a trailer. Now, assuming you have done that (but you're not supposed to), you plug in to reverse polarity and you grab the bike, nothing will happen. You just connected the hot wire straight to ground when you plugged in your trailer and the circuit breaker either popped or you melted some wires. Never bond the neutral to the ground...
Bruce
2009 6.5'X11' TTT - Boxcar
All it takes is a speck of faith and a few kilowatts of sweat and grace.
Image
Boxcar Build
aVANger Build
User avatar
bdosborn
Donating Member
 
Posts: 5494
Images: 772
Joined: Wed May 05, 2004 11:10 pm
Location: CO, Littleton
Top

12 volt side of life

Postby Dee Bee » Wed Sep 21, 2005 10:51 am

cracker39 wrote: Mike Nemeth's article on 12 volts mentions doing that, but with a 3-stage charger. I can't get his site up, and the cached version doesn't show any of his diagrams or photos.


You can find it here.
http://www.ccis.com/home/mnemeth/12volt/12volt.htm

DEE BEE
Grace happens...
User avatar
Dee Bee
500 Club
 
Posts: 696
Images: 55
Joined: Fri Jun 04, 2004 9:17 pm
Location: York, PA
Top

Postby cracker39 » Wed Sep 21, 2005 10:58 am

Thanks, Dee Bee. I got it this time. The first time i tried i was given bart.ccis.home and your link has www.ccis.home. That works. Now I can see the diagrams. :D
Dale

Sometimes I pretend to be normal. But, that gets boring...so I go back to being me.

Squidget Pop Top Build Pages http://www.thesquidget.com/ptbuild/ptbuild.html

Squidget and Pop Top Plans Info and Photos: http://www.TheSquidget.com
User avatar
cracker39
3000 Club
3000 Club
 
Posts: 3069
Images: 233
Joined: Thu Jun 30, 2005 2:18 pm
Location: Lake Alfred, Florida, USA
Top

Postby Ken A Hood » Wed Sep 21, 2005 10:59 am

My AC panel has a GFCI outlet on it; and another breaker for the Charger. But since my charger isn't hardwired, I pan on plugging it into the GFCI (When I need to charge) and use the other circuit to run the AC outlets (1 in the galley [GFCI] and 2 in the cabin run from the 1[GFCI] in the galley).
And I also took a closer look at the AC wiring in the panel, and it's all stranded wire, so I'm OK there as well.
Image
Disclaimer: I in no way resemble the avatar shown. Furthermore, I in no way have any affiliation to the Trailer Park Boys and more specifically Bubbles!
User avatar
Ken A Hood
500 Club
 
Posts: 841
Images: 42
Joined: Sun Apr 18, 2004 8:15 pm
Location: ON CANADA
Top

Postby xe1ufo » Thu Sep 22, 2005 1:04 am

Hey IraRat:

You doing o.k. with this last hurricane blowing through there? Hope so!
Blessings.
Dr. Steve
Central old Mexico
User avatar
xe1ufo
Teardrop Master
 
Posts: 186
Images: 12
Joined: Sat Jul 02, 2005 2:24 pm
Location: San Juan del Río, Queretaro, Mexico
Top

Postby IraRat » Thu Sep 22, 2005 2:01 pm

xe1ufo wrote:Hey IraRat:

You doing o.k. with this last hurricane blowing through there? Hope so!
Blessings.


Thanks for asking, Doc. We're cool.

Whether I'll survive my electrical installation, that's another matter.

But seriously, in response to the above suggestions about getting "professional help" with this, come on. What I'm doing is the simplest installation of all.

And aside from Powder, whom I trust, I guarantee you that down here in South Florida, I will find 10 electricians who will give me 10 totally different opinions.

All I'm doing is running 3 lines/circuits from a distrubution panel...positive, negative and neutral wires for each...and connecting devices to those lines that all have positive, negative and neutral connectors.

My basic question was, which I believe has been answered, is yes:

Ground the ground connectors from the panel to the steel frame.
--Ira

"My HD and Wal-Mart have been out of Titebond for weeks, and I think it's a communist conspiracy."
User avatar
IraRat
Forum Storyteller
 
Posts: 1573
Joined: Wed Apr 06, 2005 8:43 am
Location: South Florida
Top

Grounding

Postby wentzzee » Thu Sep 22, 2005 2:21 pm

Cracker 39
You got it right you don't have to frame ground if you run a ground wire thru your harness. As to the AC why would you frame ground it when your trailer is no part ot the system for an AC?
All Reality Starts with a Dream
wentzzee
Teardrop Builder
 
Posts: 28
Joined: Thu Sep 08, 2005 5:50 pm
Location: McColl SC
Top

Re: Grounding

Postby cracker39 » Thu Sep 22, 2005 3:03 pm

wentzzee wrote:Cracker 39
You got it right you don't have to frame ground if you run a ground wire thru your harness. As to the AC why would you frame ground it when your trailer is no part ot the system for an AC?


Bruce convinced me via email of the merits of grounding the 120VAC to the chassis. I still do not plan to ground my 12VDC to the ground as I will have all devices on separate two-wire circuits from the device to the fuse panel and ground terminal block, and I won't have a converter in the system. Here's my schematic:

Image
Dale

Sometimes I pretend to be normal. But, that gets boring...so I go back to being me.

Squidget Pop Top Build Pages http://www.thesquidget.com/ptbuild/ptbuild.html

Squidget and Pop Top Plans Info and Photos: http://www.TheSquidget.com
User avatar
cracker39
3000 Club
3000 Club
 
Posts: 3069
Images: 233
Joined: Thu Jun 30, 2005 2:18 pm
Location: Lake Alfred, Florida, USA
Top

Postby IraRat » Thu Sep 22, 2005 3:07 pm

Oy, that looks complicated, Dale!!!

But since I'm just doing 120, that part of your schematic is all I have to do.

So what's so complicated about THAT?
--Ira

"My HD and Wal-Mart have been out of Titebond for weeks, and I think it's a communist conspiracy."
User avatar
IraRat
Forum Storyteller
 
Posts: 1573
Joined: Wed Apr 06, 2005 8:43 am
Location: South Florida
Top

Postby cracker39 » Thu Sep 22, 2005 3:15 pm

Ira, it really isn't complicated. I'm just running two stranded 2+gound to the rear outlet and one to the front outlet, along with my 12V 2-wire runs for the lights, fans, and a 12V outlet front and rear. I'll use my 30 AMP shore power cord connected directly to the circuit breaker box. Flagship RV sells one with a plug on one end and the other end has the wires stripped ready to connect to anywhere. My only problem is that the only way I can find the stranded 2+gound is by the foot at either HD or Lowes and it is $.55 per foot for 14 gauge (ouch). Don't worry, I'll get an electrician to help me get the box and breakers connected correctly.
Dale

Sometimes I pretend to be normal. But, that gets boring...so I go back to being me.

Squidget Pop Top Build Pages http://www.thesquidget.com/ptbuild/ptbuild.html

Squidget and Pop Top Plans Info and Photos: http://www.TheSquidget.com
User avatar
cracker39
3000 Club
3000 Club
 
Posts: 3069
Images: 233
Joined: Thu Jun 30, 2005 2:18 pm
Location: Lake Alfred, Florida, USA
Top