Anything electric, AC or DC

110 ???

Postby igofshn » Thu Oct 13, 2005 4:13 pm

Getting ready to wire for 110. My intention is to have 2 plugs, one in the kitchen area and one in the sleeper. My plan is to use romex from my generator (like an extension cord) and have 2 plugs on the line. Is this going to be a problem by not having a built in circuit breaker???
igofshn
Teardrop Builder
 
Posts: 47
Joined: Sun May 08, 2005 12:28 am
Location: Lemoore, CA

Postby madjack » Thu Oct 13, 2005 4:26 pm

...doesn't your generator have a builtin circuit breaker or youu can buy a male plug with a builtin cicuit breaker and use it when you make up your power cord...I wouldn't use romex(solid wire) for your power cord...get a stranded wire cable for that
madjack 8)
...I have come to believe that, conflict resolution, through violence, is never acceptable.....................mj
User avatar
madjack
Site Admin
 
Posts: 15128
Images: 177
Joined: Thu Dec 02, 2004 5:27 pm
Location: Central Louisiana

Postby Frank » Thu Oct 13, 2005 4:34 pm

I would not use romex for an extenion cord, romex is solid copper wire and will break when bent unlike SO or SJO cord, which is fine stranded wire. As far as a breaker, unless you are making more than one circuit, other than a disconect means, don't see the need if you use # 12 awg wire on your cord and for your romex. That is good for 20 amps, you will be protected by the breaker feeding the circuit you are using, at the camp site or home, or generator. I would suggest that you make the first outlet a GFCI and down feed the second from the first, making both outlets GFCI protected.

That's the way I did mine, but there are many different opinions out there.

Frank
Last edited by Frank on Thu Oct 13, 2005 7:45 pm, edited 1 time in total.
Let's go camping!
User avatar
Frank
Silver Donating Member
 
Posts: 423
Images: 52
Joined: Wed Apr 14, 2004 9:16 pm
Location: Aiken, S.C.
Top

Postby GeorgeTelford » Thu Oct 13, 2005 7:07 pm

Hi

Always Include your own Circuit Breaker and always include RCD (residual current detection) I believe this is called GFCI in USA.

Regardless of campsite protection always include your own.

Circuit breakers are there to protect your individual lines (wires/cables) and should be rated for the appliance ampage that will be used, the campsites CB will be rated at a catch all rate for the entire rating of the supply ie if its a 16 A supply the CB will be rated in excess of 16A.

GFCI, many people cant see the point of having another when the campsite pillar as one (assuming codes same as UK regs in this respect) GFCI are Zoned ie the campsite one would need to see an higher ampage before tripping and would trip slower.

If the cable is going to be subject to movement ie flexing them multi strand is definately required, if its fixed as in behind walls run to lights and will never move again after fixing in position then solid core is OK.
User avatar
GeorgeTelford
500 Club
 
Posts: 677
Joined: Mon Jul 11, 2005 2:10 pm
Top

Postby igofshn » Thu Oct 13, 2005 9:12 pm

madjack wrote:...doesn't your generator have a builtin circuit breaker or youu can buy a male plug with a builtin cicuit breaker and use it when you make up your power cord...I wouldn't use romex(solid wire) for your power cord...get a stranded wire cable for that
madjack 8)


I'm trying to keep the electrical as simple as possible. The generator does have a built in circuit breaker.
igofshn
Teardrop Builder
 
Posts: 47
Joined: Sun May 08, 2005 12:28 am
Location: Lemoore, CA
Top

Postby mexican tear » Fri Oct 14, 2005 11:51 am

It kind of sounds to me that you want to use two (2) male plugs on the same cable. Please do not do that. It can be very dangerous. You can make a pigtail to hang out or a mountable male plug on the trailer. Then you can use a regular extension cord from the garage. Seems like the cheapest way to go to me.

kai
"Essie" and the Mexican Tear
Image
User avatar
mexican tear
Donating Member
 
Posts: 506
Images: 14
Joined: Mon May 24, 2004 12:31 pm
Location: Hardy, Arkansas USA
Top

Postby Cutterpup » Fri Oct 14, 2005 3:05 pm

igofshn
Getting ready to wire for 110. My intention is to have 2 plugs, one in the kitchen area and one in the sleeper. My plan is to use romex from my generator (like an extension cord) and have 2 plugs on the line. Is this going to be a problem by not having a built in circuit breaker???


Is it your intension to have a semi-permenant extension cord running in your TD? If that is what you want then just make sure you use stranded wire in the cord vs any type of solid wire as the vibrations will break the wire. As for a circuit breaker being needed as long as either the generator or the campground electrical supply post has one you wont need another, but if you ever find a post without a circuit breaker on it find another way to hook up power.

Dan
User avatar
Cutterpup
Teardrop Master
 
Posts: 239
Images: 15
Joined: Sat May 07, 2005 4:51 pm
Location: Annapolis, Maryland
Top

Postby cracker39 » Fri Oct 14, 2005 3:30 pm

I finally ran into an RV dealer whose parts man would actually talk to me (a builder, not an RV buyer) and answer my 110VAC questions. He can sell me a 25' shore cable (HD extension cord) with a 30amp plug on one end and stripped wires on the other ready to hook up to my trailer. He suggested getting a "4 inch box" from HD with a 30 amp breaker to wire into. After talking to him, I will wire up my 25' cable to extend out of the side through one of those plastic box inserts with a door. When the cord is not in use it will be pulled inside through the little access door and coiled in a storage compartment.
Dale

Sometimes I pretend to be normal. But, that gets boring...so I go back to being me.

Squidget Pop Top Build Pages http://www.thesquidget.com/ptbuild/ptbuild.html

Squidget and Pop Top Plans Info and Photos: http://www.TheSquidget.com
User avatar
cracker39
3000 Club
3000 Club
 
Posts: 3069
Images: 233
Joined: Thu Jun 30, 2005 2:18 pm
Location: Lake Alfred, Florida, USA
Top

Postby cracker39 » Fri Oct 14, 2005 3:30 pm

I finally ran into an RV dealer whose parts man would actually talk to me (a builder, not an RV buyer) and answer my 110VAC questions. He can sell me a 25' shore cable (HD extension cord) with a 30amp plug on one end and stripped wires on the other ready to hook up to my trailer. He suggested getting a "4 inch box" from HD with a 30 amp breaker to wire into. After talking to him, I will wire up my 25' cable to extend out of the side through one of those plastic box inserts with a door. When the cord is not in use it will be pulled inside through the little access door and coiled in a storage compartment.
Dale

Sometimes I pretend to be normal. But, that gets boring...so I go back to being me.

Squidget Pop Top Build Pages http://www.thesquidget.com/ptbuild/ptbuild.html

Squidget and Pop Top Plans Info and Photos: http://www.TheSquidget.com
User avatar
cracker39
3000 Club
3000 Club
 
Posts: 3069
Images: 233
Joined: Thu Jun 30, 2005 2:18 pm
Location: Lake Alfred, Florida, USA
Top

Postby GeorgeTelford » Fri Oct 14, 2005 3:37 pm

Hi Cracker

OK initial 30 Amp Breaker, that means you could have 3 KW of heat heating in the cable and causing a fire and the breaker still will not cut off, if your were suffering a 30 Amp shock again it will not break, bear in mind it only requires a few Milliamps to stop your heart.


A GFCI could save your life, even if you wont put smaller spur breakers in at least use some residual current detection.
User avatar
GeorgeTelford
500 Club
 
Posts: 677
Joined: Mon Jul 11, 2005 2:10 pm
Top

Postby cracker39 » Fri Oct 14, 2005 4:36 pm

Oh Boy...here we go again... George, I thought I had this all worked out. the 30amp main breaker will be located where the shore power comes into the cabin. I will be plugged into 30amp shore power at the camp site and the camp connection should have it's own breaker, and mine is a backup for my trailer's protection. Are you saying I need a larger main breaker than 30 amps? That's the rated power I am receiving from the camp. From my main breaker, the shore power will go to the AD/DC converter where there are 4 AC mini breakers (I'll use only two of them) for the circuits that will go to my front and rear 110VAC outlets which will be GFCI. I won't be pulling more than 20 amps even with a toaster oven (1500 watts/13.6 amps) and A/C (515 watts/5 amps) being used simultaneously, and each will be on it's own 15 amp circuit breaker. That works in my house, why not in the trailer? Of course, my house has a larger main breaker, as It is supplying many more appliances (fridge, freezer, electric range/oven, A/C, TVs (4)Computers (2), lights, power tools, etc, etc.) than my trailer will be. My trailer will only have one or two appliances in use, and they are small ones.

Why isn't a 30 amp main breaker large enough? What did I miss this time?
Dale

Sometimes I pretend to be normal. But, that gets boring...so I go back to being me.

Squidget Pop Top Build Pages http://www.thesquidget.com/ptbuild/ptbuild.html

Squidget and Pop Top Plans Info and Photos: http://www.TheSquidget.com
User avatar
cracker39
3000 Club
3000 Club
 
Posts: 3069
Images: 233
Joined: Thu Jun 30, 2005 2:18 pm
Location: Lake Alfred, Florida, USA
Top

Postby mikeschn » Fri Oct 14, 2005 4:41 pm

cracker39 wrote:Why isn't a 30 amp main breaker large enough? What did I miss this time?


Because the campground offers 50 amps? :rofl:

Mike...
The quality is remembered long after the price is forgotten, so build your teardrop with the best materials...
User avatar
mikeschn
Site Admin
 
Posts: 19202
Images: 479
Joined: Tue Apr 13, 2004 11:01 am
Location: MI
Top

Postby GeorgeTelford » Fri Oct 14, 2005 4:53 pm

No When you have 30 Amps coming in thats the size of main breaker you need.

Also you should have a GFCI this detects any lost ampage even a tiny amount and cuts the power extremely rapidly, this is the one that will save your life (Breakers only protect wire and appliances)

Next for each spur you should have a breaker set at that spurs maximum so say the appliance run on one spur only needs 10 Amps that spur should have a 10 Amp breaker.

Below is a link to a big thread on electrics 12v and 120 v the link takes you to page 8

http://www.tnttt.com/viewtopic.php?t=1941&postdays=0&postorder=asc&start=105
User avatar
GeorgeTelford
500 Club
 
Posts: 677
Joined: Mon Jul 11, 2005 2:10 pm
Top

Postby TomS » Fri Oct 14, 2005 7:36 pm

Dale,

It may help if you think of GFCI's as leak detectors. The GFCI compares the current passing between the positive and negative side of the circuit. If the device detects any difference between the two legs, it shuts down the circuit immediately. They are typically used in areas such as kitchens, bathrooms, outdoor areas where there is a higher risk of shock.

As others have said, don't count on that 30 amp main breaker to protect you from a fatal shock. The amount of current required to induce cardiac arrest, is many times less that the amount required to trip that 30 amp main breaker.

There are several ways to incorporate GFCI protection into your Squidget. In my Cubby, I use a GFCI protected extension cord. You can also get circuit breakers with GFCI protection and GFCI protected outlets.
Tom Swenson
[email protected]
User avatar
TomS
1000 Club
1000 Club
 
Posts: 1367
Joined: Thu Nov 18, 2004 2:06 pm
Location: Fitchburg, MA
Top

Postby bdosborn » Fri Oct 14, 2005 11:58 pm

George,

A 30 amp breaker will be fine as long as you use 30A wire, which would be a #10 or better, from the pedestal to your breaker. Just make sure that you have the correct plug for the pedestal end. A 30 amp plug is different from a 20 amp. Then you'll need to use 30A wire from the 30A breaker to your 20A breakers. Use #12 wire from the 20 amp breakers to your receptacles. If you don't want to use GFCI breakers (a 30A is kind of expensive) use GFCI receptacles. To be honest, I don't see a need for the 30A breaker in your trailer as long as all the wires to the line side of your 20A breakers is #10. The only thing the 30A will protect is the short run of wire from the 30A to the 20A breakers. But, NEC requires a main breaker for trailers, FWIW.
Bruce
2009 6.5'X11' TTT - Boxcar
All it takes is a speck of faith and a few kilowatts of sweat and grace.
Image
Boxcar Build
aVANger Build
User avatar
bdosborn
Donating Member
 
Posts: 5492
Images: 767
Joined: Wed May 05, 2004 11:10 pm
Location: CO, Littleton
Top

Next

Return to Electrical Secrets

Who is online

Users browsing this forum: No registered users and 5 guests